bobodu wrote:The picture helps....I see that one terminal is NOT USED...So you would need a pigtail to plug in a drill...
Every genset I have seen had a couple of 115 taps plus the four prong.....that's where I was getting lost
KE4AVB wrote:38racing,
What you have is a bonded Neutral setup; otherwords, Ground and Neutral are tied together somewhere. Four wire plugs uses what is called a floating neutral setup which may be still be bonded if the ground and the neutral are tried together somewhere in the generator. Most electrical setups usually have the Neutral and Ground tried together at your home electrical circuit breaker panel. The prefer method of connecting is to have the neutral floating at the generator where you can and need to earth ground the chassis.