Not for generators. Most generators run at a fixed speed no load around 3750 RPM to achieve 60Hz output under load (3600 RPM/60 = 60Hz) - Some such as diesel generators and other 4-pole gensets may run at 1875 RPM1 top no load (1800 RPM/30 = 60Hz) SOME generators, usually the pricier ones , may have an "auto Idle" feature to idle down the generator when there's no load, but even those will run top no load at start up until auto idle kicks in.
The governor should work to MAINTAIN that top no load RPM (you need a tach at minimum, or better, a Kill-A-Watt meter or multimeter that can measure frequency in Hz) but it should not exceed it. If measuring Hz, you want it to be around 62 Hz unloaded, so when it takes on a load, it drops to around 60hz
If the generator is working properly for power output and generation, then there's nothing much to fix.