Gary Greathouse wrote:the code is 80 12 05, Sory it took so long to get back has been a BZ week lol. Well I got it running great the only prob is the gov. It only works part of the time under a load, I noticed the spring looks a little stretched could that be the prob? I already adjusted the static and changed the spring around to diff holes with no luck lol. Any ideas? When first put under a load it stays at idle for about 30 seconds then to about 1/4 throttle for 5 sec. and back to idle and repeat.
Sounds like what we call a surge. You need a tachometer, or considering it is a generator, a hertz meter
when nothing plugged in on it, should be around 3750 RPM, or about 62 Hz at 120v output, unless an auto idle is present. when under a load, should be around 3600 RPM or 60Hz output (assuming this is a North America application - U.K. needs 50Hz, so RPMS would be slower)
Once you got that set, if it is still doing as you describe (surging) that is usually indicative of a fuel starvation issue. If you get the RPM set right after a static governor adjustment, should not be a governor issue. - way to tell is to put a finger on the throttle lever and hold it in place to keep it from moving, and see if the engine starts to die out or sputter or not run smoothly - if it does the problem is not the governor, but if it runs fine when holding throttle steady, you have some sort of governor issue - changing the location of the hole the spring hooks in the governor arm is just changing the sensitivity (Governor droop)